Hmmm what's wrong with 30A fuses?Yes, all of the 30a fuses!
True maybe. But I think this panel is located in the laundry room so maybe that's why there's 30A fuses.It could be fine but given the number of 30 amp fuses you have to wonder if some of those circuits are over-fused and the conductors are smaller than #10.
I'm guessing it's a residence, and it wasn't wired with all #10cu.Hmmm what's wrong with 30A fuses?
But probably not 30 amp wire.Hmmm what's wrong with 30A fuses?
True maybe. But I think this panel is located in the laundry room so maybe that's why there's 30A fuses.
That’s what I’ve done before.You could put the correct type S adapters in to limit the ampacity of the fuse to the ampacity of the wire.
I just had someone ask me to help them remove the S adapters. I asked why, they said it was so they could put in larger fuses….You could put the correct type S adapters in to limit the ampacity of the fuse to the ampacity of the wire.
I rest my case.I just had someone ask me to help them remove the S adapters. I asked why, they said it was so they could put in larger fuses….