Any requirement in NEC 2017 for something like this

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Attached sketch shows 800A meter stack over six feet wide in electrical room. The width between meter stacks and electrical room is 15.22 inches. Person cannot get into bottom space

Question:

1 Assume that breakers and meters are facing label S1 then would width of 15.22 inches be enough? Is their any requirement in NEC 2017?

2. Assume that breakers and meters are facing label S2 then would width of 15.22 inches be enough to get out of bottom space? Is their any requirement NEC 2017?

a5b1e55bb09c8ab70eda52918aac9051.jpg
 

pv_n00b

Senior Member
Location
CA, USA
Occupation
Professional Electrical Engineer
Outside of the NEC requirements, do you really want to put someone back there with an arc flash event and expect them to get out? Just because you can do something does not mean you should. ;) And yes 110.33(A) requires 24".
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
H Hsting is a plans reviewer not the designer, he posts lots of sketches of oddball situations for us to mull over.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Outside of the NEC requirements, do you really want to put someone back there with an arc flash event and expect them to get out? Just because you can do something does not mean you should. ;) And yes 110.33(A) requires 24".

110.33 is for medium voltage over 600V no? I dont have NEC 2017 with me. What I have is 208/120V three phase less than 600V
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
110.33 is for medium voltage over 600V no? I dont have NEC 2017 with me. What I have is 208/120V three phase less than 600V
Thats why I posted 110.26(C)(1), you'll need to interpret 'sufficient area'. The width of a door to the electrical room seems reasonable in that case.
 