Gentlemen, I need your advice on an electrical solution to solve a problem I am having. While the problem is more mechanical in nature I can’t address it that way.
I have a float switch that is mounted on a boiler. This float switch sends 120 VAC to the coil of a motor starter. As the water level starts to rise in the boiler the float starts bouncing, causing the motor starter to chatter badly. At times the contacts in the motor starter are welding themselves together. There are things that have changed on the boiler(s); new (excessive) loads, old floats switches were mercury bulbs and new ones are snap switches, water chemistry (well let’s not go there). While it isn’t the right way I need to consider an electrical solution, provided it is safe/legal.
I’m proposing to install a time delay relay across float switch contacts. This way the float switch would still operate feed water pump motor starter if time delay relay failed. It looks like an off delay, with power trigger (S break), is what I need. I would want the time delay quite short, just long enough to cover any bounce in the float switch.
Just to be clear, assume float switch calls for the pump to start every sixty seconds. Pump runs an average of 11 seconds. During the last two to three seconds of pump operation, motor starter drops in an out repeatedly. I’ll install the time delay relay in parallel with float switch. Input voltage will be a continuous 120 VAC. The float switch will provide a 120 VAC power trigger to the time delay relay. Time delay will be set rather short, say 0.25 seconds. Upon closure of float switch, trigger is energized and relay contacts close. Once float switch opens and trigger is removed, and relay contacts start timing open…..unless trigger is closed again before timing out, in which case time delay is reset and relay contacts stay closed until trigger is removed for time exceeding the time delay setting.
So, what do you guys think? Is it safe/legal? Am I picking the right time delay relay type? If said relay is a “universal” voltage (24-240 VAC) will the bouncing float switch let voltage drop enough to reset time delay or should I look for something that only uses a 120 VAC trigger? Any better (electrical) ideas on how to solve my problem?
BTW, pump is 3 phase, 480 VAC, size one NEMA motor starters with electronic overload relay.
I have a float switch that is mounted on a boiler. This float switch sends 120 VAC to the coil of a motor starter. As the water level starts to rise in the boiler the float starts bouncing, causing the motor starter to chatter badly. At times the contacts in the motor starter are welding themselves together. There are things that have changed on the boiler(s); new (excessive) loads, old floats switches were mercury bulbs and new ones are snap switches, water chemistry (well let’s not go there). While it isn’t the right way I need to consider an electrical solution, provided it is safe/legal.
I’m proposing to install a time delay relay across float switch contacts. This way the float switch would still operate feed water pump motor starter if time delay relay failed. It looks like an off delay, with power trigger (S break), is what I need. I would want the time delay quite short, just long enough to cover any bounce in the float switch.
Just to be clear, assume float switch calls for the pump to start every sixty seconds. Pump runs an average of 11 seconds. During the last two to three seconds of pump operation, motor starter drops in an out repeatedly. I’ll install the time delay relay in parallel with float switch. Input voltage will be a continuous 120 VAC. The float switch will provide a 120 VAC power trigger to the time delay relay. Time delay will be set rather short, say 0.25 seconds. Upon closure of float switch, trigger is energized and relay contacts close. Once float switch opens and trigger is removed, and relay contacts start timing open…..unless trigger is closed again before timing out, in which case time delay is reset and relay contacts stay closed until trigger is removed for time exceeding the time delay setting.
So, what do you guys think? Is it safe/legal? Am I picking the right time delay relay type? If said relay is a “universal” voltage (24-240 VAC) will the bouncing float switch let voltage drop enough to reset time delay or should I look for something that only uses a 120 VAC trigger? Any better (electrical) ideas on how to solve my problem?
BTW, pump is 3 phase, 480 VAC, size one NEMA motor starters with electronic overload relay.