appreciate any experience you may have on this subject....
The AHJ has decided to implement on a small commercial occupancy,
the "Neutral Fault Test"
the building is 30 years old. it is being brought up to current codes,
with special attention being given to Title 24 compliance.
The inspector has stated that the "neutral fault test" will be performed.
here is the drill, and logic behind it....
as the grounded conductor, and grounding conductor serve separate
functions, and should not be joined together in the field wiring, it should
be possible to lift the feeder neutral in a panel, and read no conductivity
between the neutral bus, and the ground bus. infinite resistance.
and that is what the inspector is going to watch me do. he will not
sign off the electrical permit without this test being performed to his
satisfaction.
anything other than infinite resistance will require the wiring of the
building to be corrected until this fault is cleared.
and, on the engineered drawings, where the city's stamp is affixed, it
is noted by the approving plan checker that "neutral fault test is to be
performed". so, it is sanctioned by the powers that be.
any of you guys have experience with this?
.... i have only found this "neutral fault test" performed in one locality...
and i've worked in a lot of places. thanks for any feedback you may have.
The AHJ has decided to implement on a small commercial occupancy,
the "Neutral Fault Test"
the building is 30 years old. it is being brought up to current codes,
with special attention being given to Title 24 compliance.
The inspector has stated that the "neutral fault test" will be performed.
here is the drill, and logic behind it....
as the grounded conductor, and grounding conductor serve separate
functions, and should not be joined together in the field wiring, it should
be possible to lift the feeder neutral in a panel, and read no conductivity
between the neutral bus, and the ground bus. infinite resistance.
and that is what the inspector is going to watch me do. he will not
sign off the electrical permit without this test being performed to his
satisfaction.
anything other than infinite resistance will require the wiring of the
building to be corrected until this fault is cleared.
and, on the engineered drawings, where the city's stamp is affixed, it
is noted by the approving plan checker that "neutral fault test is to be
performed". so, it is sanctioned by the powers that be.
any of you guys have experience with this?
.... i have only found this "neutral fault test" performed in one locality...
and i've worked in a lot of places. thanks for any feedback you may have.