What do you do about machines that move around? They want to use SJ cord as drop cords to a rec.
One of the plants I work in has several smaller machines mostly 3 ph 30 amp max and 120v drops for convienience outlets.
The engineer designed a distribution set up with a unistrut trapeze and a 6x6 wireway.
We built a unistrut trapeze open end up,where the 2 long runners 60' long ran east and west. then put full 10' cross pieces every
5' running north and south to tie the east and west runners together. The 6x6 gutter ran east and west in the center of the trapeze fastened to the crosspieces with bolts and springnuts. The gutter was fed from a LV 120/208V and a HV 480v panel to get the circuits needed to the gutter for distribution. Wherever there was a machine drop, we would take a 6' piece of 3/4" emt with a short
90d bend on the end compression connector into the gutter and strut strapped to the long runner. On the end of the 90d bend
we installed a 4 square box with a blank cover and brought the cord out of the bottom of the 4 square then back to a kellem grip hanging from the long runner down to the machine or twistlock or whatever. What we did do instead of bringing the circuits directly to the 4 square boxes at the machine location was to chase nipple 4 square boxes face down up into the bottom of the gutter every 4'.
That way the circuits remained in those 4 square boxes with the lid labeled and the gutter was just used as a raceway so there werent an overload of splices in the gutter,, the junction was made in the 4 squares nippled into the bottom of the gutter and kept it very clean.
Otherwise Rigid anywhere outside, on the roof or in the classified areas, emt inside with compression fittings only, black for all 480v wiring, Red for all 120v wiring excluding neutrals and Blue for all 24v control wiring.