I have 3- 4" with 4- 500's feeding in the back and the same thing going out the top. would a 24x24x10 do it
In this case there is no "fill" issue. That only applies when the conductors are #6 and smaller.If it looks to full, it probably is. But that's just from an inspectors stand point.
If it looks to full, it probably is. But that's just from an inspectors stand point.
In this case there is no "fill" issue. That only applies when the conductors are #6 and smaller.
The issue we have here is the space between the conduits that contain the same conductor and the bending space for the conductors based on the exception for angle or U pulls.
It doesn't matter what it is called. There are no volume calculations for conductors #4 and larger.The OP also said, Jbox, what he really meant then was, pull box.