68Malibu383
Member
- Location
- Raleigh, NC
Can anyone tell me when code required a light and receptacle on a rear porch? Thanks!
There is a section that requires controlled (switched) light at residence outside doors.
There is another section that requires a receptacle within a specified distance of the door, on the outside.
Tapatalk!
I think it was either the 1996 or 1999 code cycle that added the requirement to have a receptacle at both the front and back of a dwelling at grade level, but before this only one was required and could be anywhere outside as long as it was at grade level, I remember the change just not which code cycle it was put in, I know the 1993 didn't require it, but not sure if the 1996 did?
Kwired, you do bring up some important limitations to what the NEC actually requires.
One requirement has you put an outdoor receptacle, accessible from GRADE, on the front and rear of a house. It's quite possible, in a duplex, that neither of these would be on the same side of the house as the door. It's quite possible that a receptacle placed on the porch would not qualify, as it would not be accessible from grade.
Likewise, the light need not be specific to the door, or switched anywhere near the door. It's common for a single light to serve, say, a patio door and a door not associated with the patio.
The 'switch' requirement can be met with timers, photocells, or motion sensors. It need not be a toggle switch on the wall.
I don't know what led the OP to ask his question, so I'll repeat what the first part of the NEC tells us: the Code is NOT a design manual. That's not it's job. "Code minimum" is almost always crappy design.