- Location
- Eastern Oregon
- Occupation
- Electrician
It has the 4 buss bars that run underneath it. Looking through the parts sent with the crane it looks like each buss has a lug that clamps to the end of it. We've read through the code book and it looks like we're going to stub a pipe pretty close to the bussing, bond bush the end of it, and then sleeve some MC through it(jacket removed), right to the buss. Seems weird to me leaving exposed conductors out in the open, even though it's probably 20' off the ground, but 610.11(B) seems to allow it for short lengths. We ran our idea by our inspector today and he was okay with it.
I'm just wondering if this is how everyone else usually does this?
Thanks.
I'm just wondering if this is how everyone else usually does this?
Thanks.