1) schedule 80 is not necessarily required.
3) main breaker is often required to allow disconnection of the structure by no more than 6 throws of the hand
if using a tap rule
Correct me if I am wrong.
The OP stated that this Garage is Attached, There is no need for a main Breaker, There is no need for rods or GEC.
All that is needed is a proper ground wire sized for the circuit.
agree..I had to look twice... picture is correct as far as I can see for an ATTACHED garage.I agree it says attached. The going into the ground with the conduit is deceiving.
Better to have and not need, than need and not have.
I can give numerous situations such as this, and take a survey of a dozen experts on the NEC. Half of them will say it is subject to physical damage, half of them will say it isn't. If you've got schedule 40 risers, you better hope that your inspector is part of the half of them who say it isn't. Better to have and not need, and be covered no matter what the opinions of the inspector.
Adding "extra" grounding electrodes is not dangerous and is not prohibited by the NEC.
One inspector mentioned that in a fault or Lightining having a rod a the service and at the pedestal is dangerous
I posted that for the following reason: here in WA: inspector A required another rod at the garage, inspector B required an extra rod 6' away from the existing rod at the pedestal/service, inspector C does not required extra rod at the pedestal (only the existing one at the service) and in another occasion in another state, inspector D required 2 rods at the garage (main service at the house had already 2 rods and bonded to water pipe and inspector E stated very firm that will not accept another rod besides the one at the service/disconnect because it is dangerous.
So, who should I listen to? How "dangerous" is the last quote?