Anything wrong with doing this? Transf. connections

Status
Not open for further replies.

designer82

Senior Member
Location
Boston
Need to run 4160v to a load and and also step down to other loads as shown.

Does this look ok, any issues with it?

Thanks
 

Attachments

  • transf question.png
    transf question.png
    44 KB · Views: 0

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
As long as the breaker upstream on the 4160V side is sized to protect the wires serving the transformer primary and the wires serving the 4160V load, I think this is OK. I don't like it that much, however. In order to turn off one item, you need to turn off both.
 