I have always put the panels in each unit. Can they be put in the basements?
240.24(B) Occupancy.
Each occupant shall have ready access to all overcurrent devices protecting the conductors supplying that occupancy.
Exception No. 1: Where electric service and electrical maintenance are provided by the building management and where these are under continuous building management supervision, the service overcurrent devices and feeder overcurrent devices supplying more than one occupancy shall be permitted to be accessible to only authorized management personnel in the following:
(a)Multiple-occupancy buildings
(b)Guest rooms of hotels and motels that are intended for transient occupancy