Apartment building electric service

Status
Not open for further replies.

ammklq143

Senior Member
Location
Iowa
Occupation
Electrician
I have a customer asking about an estimate for a building he would like to convert to apartments. There would be 6 meters/disconnects for the apartments and each apartment would have a 100 amp panel. There would also be 1 meter/disconnect for the common area for a total of 7 meter/disconnects. I've not done an apartment of more than three so I'm curious how others would build the electrical service with the meters and disconnects. I haven't found a ganged meter socket with more than six sockets so would I be able to use a six gang socket and then feed out of that to a single for the common or.....? Any suggestions would be appreciated.

Thank you.
 
I have a customer asking about an estimate for a building he would like to convert to apartments. There would be 6 meters/disconnects for the apartments and each apartment would have a 100 amp panel. There would also be 1 meter/disconnect for the common area for a total of 7 meter/disconnects. I've not done an apartment of more than three so I'm curious how others would build the electrical service with the meters and disconnects. I haven't found a ganged meter socket with more than six sockets so would I be able to use a six gang socket and then feed out of that to a single for the common or.....? Any suggestions would be appreciated.

Thank you.

No. You would be over the six disconnect rule for service disconnects. NEC 230.71(A) You would need a main disconnect ahead of the meter stack.
 