Re: Apartment Building Grounding
This is an interesting question in as far as having five service laterals to the same building for 100 amp services.
Each service is required when grounded to have a connection to the available grounding electrode(s).
Each service you connect to the cold water. You will be required to supplement the cold water with another electrode, which as you stated is a groundrod. The question is, are six different ground rods required? IMO one ground rod would suffice and an additional ground rod bonded to that one as per 250.56 if the 25 ohms to ground is not measured.
Pierre
After reading your post again and remembering how different other parts of the country perform the work, more details of how the building is supplied with the cold water, and how the building is divided into the five units is necessary to provide a more thorough answer.