mkgrady
Senior Member
- Location
- Massachusetts
I install a lot of 30 amp 125/250 volt inlets for homes and use an interlock between the MCB and generator breaker in the main panel for a home. This is a pretty inexpensive job for a customer and they are left with the flexibility to turn on whatever the generator can handle. I coach the customer on what can be run off the generator without overloading it.
Now I'm looking at a job to bid to power an apartment building. Actually there are three buildings of about 45 apartments each. They suffered through an outage last winter and eventually brought in a temp generator for each building to power the boiler room and the public area lights. The buildings were not set up to connect generators so there was a lot of temp cords running around the electric room and open panel covers to make the temp connections. I was not involved with any of that work. I'm told the town government is pressing the management company to be ready for the next outage by installing power inlets to simplify and make safe the connection of generators next time they loose power.
So my question is can this be done simply like I would power a home? Can I somehow interlock the main with a generator feeder? Would a Kirk Key Interlock type thing work or something like that? The alternative to an interlock is going to be a lot of work. Each building has a 120/208 volt, 1200 amp service with a three section switchboard (GE THFB Panelboard 1981 vintage) One section is the incoming underground feed and the main switch. The other two sections feed all the apartments, elevator, common lighting panel and boiler panel. They only want to feed the boiler panel and the common area lighting panel and in one building they want to feed a common kitchen area so the residents from all three buildings can eat in an emergency situation.
The alternative to an interlock will entail re-feeding these critical loads from a new panel that will be powered through a manual transfer switch. Normal power will come from a new circuit in the existing switchboard and emergency power will come from the generator inlet. Seems if there is an easier way to do this they could save a ton of money. They just turned down an offer from another company north of 100 grand to install three standby generators due to the cost.
Now I'm looking at a job to bid to power an apartment building. Actually there are three buildings of about 45 apartments each. They suffered through an outage last winter and eventually brought in a temp generator for each building to power the boiler room and the public area lights. The buildings were not set up to connect generators so there was a lot of temp cords running around the electric room and open panel covers to make the temp connections. I was not involved with any of that work. I'm told the town government is pressing the management company to be ready for the next outage by installing power inlets to simplify and make safe the connection of generators next time they loose power.
So my question is can this be done simply like I would power a home? Can I somehow interlock the main with a generator feeder? Would a Kirk Key Interlock type thing work or something like that? The alternative to an interlock is going to be a lot of work. Each building has a 120/208 volt, 1200 amp service with a three section switchboard (GE THFB Panelboard 1981 vintage) One section is the incoming underground feed and the main switch. The other two sections feed all the apartments, elevator, common lighting panel and boiler panel. They only want to feed the boiler panel and the common area lighting panel and in one building they want to feed a common kitchen area so the residents from all three buildings can eat in an emergency situation.
The alternative to an interlock will entail re-feeding these critical loads from a new panel that will be powered through a manual transfer switch. Normal power will come from a new circuit in the existing switchboard and emergency power will come from the generator inlet. Seems if there is an easier way to do this they could save a ton of money. They just turned down an offer from another company north of 100 grand to install three standby generators due to the cost.