hypothetical question.
4 apartments -1 common area, 900 sq.ft each, common laundry, all gas heat- water-range, no A/C.
Main service disco, discos-sub meters-feeders to each apt and common area.
Apt load.
900sq.ft x 3VA=2700VA
2 SABC=3000 VA
HVAC load 500VA
Largest motor = HVAC=125% already added
5700VA-3000VA=2700VA
2700VA x .35 = 945VA
3000VA + 945VA + 500VA
total 4445VA/240V=19A
What size feeders and panel does apt need?
In short, are these feeders required to be sized to 230.79? 100 amps, 60 amps, or.....