Feel somewhat un educated posting this but my experience has been heavy industrial and single family homes. That being said I have a load calculation question on a 6 unit apartment building.
Specs are as follows 6 units 900sq ft each. Kitchen with gas range. fixed in place appliances are dishwasher and microwave. There is a gas furnace in each unit, there is no air conditioning. 2 bedroom 1 bath. The laundry is in the unfinished basement.
Any ideas on approximate feeder size and amperage for the entire apartment complex..im not looking for someone to do the work for me but the number I cam up with seems very low.
2700va gen light..3000 small app..1500 microwave with 35% after first 3000 I came up with 4,470va per unit works out to 18.625 amps
Entire building load without house power worked out to 71.125 amps.
Do these numbers sound reasonable?
This is my first time doing a multifamily load calc other than on my test. I used annex d Example D4(a) Multifamily dwelling.
Thanks
for all the help
Specs are as follows 6 units 900sq ft each. Kitchen with gas range. fixed in place appliances are dishwasher and microwave. There is a gas furnace in each unit, there is no air conditioning. 2 bedroom 1 bath. The laundry is in the unfinished basement.
Any ideas on approximate feeder size and amperage for the entire apartment complex..im not looking for someone to do the work for me but the number I cam up with seems very low.
2700va gen light..3000 small app..1500 microwave with 35% after first 3000 I came up with 4,470va per unit works out to 18.625 amps
Entire building load without house power worked out to 71.125 amps.
Do these numbers sound reasonable?
This is my first time doing a multifamily load calc other than on my test. I used annex d Example D4(a) Multifamily dwelling.
Thanks
for all the help