I was asked to do a load calculation on a 15 unit apt with electric range dishwashers and disposal but no specs were given is there a general rule or a common kva for the every standered range when i have a print but no appliance specs
 

mdshunk

Senior Member
Location
Right here.
By the time you apply the range demand factors for 15 electric ranges, it won't make that much difference whether you pick 8, 10, or 12 KW. Table 220.19
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
mdshunk said:
By the time you apply the range demand factors for 15 electric ranges, it won't make that much difference whether you pick 8, 10, or 12 KW. Table 220.19
But it will make a difference when you calculate the feeder to each unit.
 