Apartment panel calc
Toros
Tujunga, CA
Hi,
about the calculation of sub panel in apartment,
supplied through 120/208v, 1ph, 3wire feeder;
should I divide total loads in volt-amp to 208v
(example: 15000VA / 208v= 72 A)
Thank you
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
Hi,
Thank you
Yes since you are using 2 hots and a neutral so the load is distributed between both conductors