Hello Everyone,
I have a question I know someone here will be able to answer. I have an APC rackmount UPS (MN: SUA1000RM2U). Tonight, I decided to put my fluke 87 on its output to check its voltage voltage when I noticed a potential design flaw. When the UPS is running on normal power, I get 120v between hot and neutral and 120v between the hot and EGC, but when the UPS is running in battery mode, I only read 58v between the hot and EGC.

From my current knowledge of electrical, I can't figure out how this UPS could safely clear a fault between the hot and the EGC in battery mode.

Am I missing something, or is this a design flaw?

Thanks!
Jacob
 

dbuckley

Senior Member
The Real Deal with UPSs is how much current they can generate into a bolted fault whilst running off batteries. Some UPSs supply this data, others dont. It's normally stated at something like 500% for 5 cycles. So, your 10A UPS can supply 50A for 1/12th of a second before collapsing. Will the 10A MCB open in that time at that overload? I don't know, check your curves. But after 1/12th of a second, the UPS has gone into shutdown anyway...

If the mains is present, and a fault occurs, the UPS will go into bypass and let utility power clear the fault.

UPSs are quite some way from the infinite grid.
 

ELA

Senior Member
Occupation
Electrical Test Engineer
This seems to imply that the UPS output is isolated from ground.
The 58 volts is probably not "real" if measured under load (or with a wiggy) it would most likely go to zero.

So ... could there even be a fault current to ground when running on Battery?

Seems to me that the output breaker is only intended for a hot to neutral fault since the output neutral is not bonded to ground.
 