Elect117
Senior Member
- Location
- California
- Occupation
- Engineer E.E. P.E.
Actually there are no line to neutral loads the switchgear so there was no need to have a grounded conductor (grey) from the XFMR center tap. There is however a green grounding conductor (basically the SSBJ) that ties to the neutral to the ground buss in the swgr
Sent from my iPhone using Tapatalk
I feel like I am only getting some of the grounding information. I can't tell if you understand what makes a service grounded or ungrounded.
1) Grounding electrode at transformer is directly connected to transformer neutral winding ?
2) Transformer case is bonded to the SSBJ from the transformer to the switchgear?
3) The green wire from the transformer to the switchgear and it is landed where at each location?
4) The switchgear has a main bonding jumper between the neutral bar and the equipment grounding bar?
5) The building's grounding electrode system is bonded in the switchgear to the ground bus which has a main bonding jumper to the neutral bar?
Not earthing the center tap of the transformer is the definition of having a ungrounded service. Not running a conductor from the transformer center tap to the switchgear's neutral or the switchgear's main equipment grounding bar will create problems. (Or the normal ungrounded stuff is needed).
Last edited: