Hey all, I'm new to the board and figured I'd ask some pros.
Apparently today I learned something. Not sure I like it though. It has been my understanding that a motor circuit can be rated as high as 125% of the circuit rating. I know the standard is FLA is 80% of the breaker rating. I learned today that you only have to upsize the breaker leaving the wire too small. I see occasionally a 30a breaker w/12 AWG or a 40a w/10AWG. Aren't thermo breakers designed to handle inrush loads. I typically see this on A/C condensers and well pumps. 240v/1Ph. The breaker is supposed to protect the wiring. Now, not only does the current have to rise from say 16a to 20-24a to trip a 20a breaker it now has to rise an additional 10a for a total of 14a to trip a 30a, I would think that would let some smoke out. Can anyone explain this. I have been talking to others and the answers are every which way. They are citing code that seems to go in circles, or is that my head. Anyway, I've lined up those 6 brain cells I got. I'm ready to listen.
Apparently today I learned something. Not sure I like it though. It has been my understanding that a motor circuit can be rated as high as 125% of the circuit rating. I know the standard is FLA is 80% of the breaker rating. I learned today that you only have to upsize the breaker leaving the wire too small. I see occasionally a 30a breaker w/12 AWG or a 40a w/10AWG. Aren't thermo breakers designed to handle inrush loads. I typically see this on A/C condensers and well pumps. 240v/1Ph. The breaker is supposed to protect the wiring. Now, not only does the current have to rise from say 16a to 20-24a to trip a 20a breaker it now has to rise an additional 10a for a total of 14a to trip a 30a, I would think that would let some smoke out. Can anyone explain this. I have been talking to others and the answers are every which way. They are citing code that seems to go in circles, or is that my head. Anyway, I've lined up those 6 brain cells I got. I'm ready to listen.