Got a call last night from a frequent landlord client of mine. She said that the appliance man got electricuted and left the premises, and now the tenant doesnt have any heat in the house. And also she said "by the way, I want you to rebuild the service as soon as you can".....
So I got there, I asked what happend...the tennant said that they rented a dryer from a rent-to-own place, and the delivery guy had to put the cord on the dryer. Then he had to make an adjustment to the connection and it shocked him really bad, and he left. So I asked, "he did this while it was plugged in"? and they said yes....
So after checking checking around with my trusty wiggy, I find that there is no 240v in the house, only one leg or phase is hot, the other is very weak. So this leaves the hvac and the dryer unfunctional...
So this eventualy takes me out to the pole in the back yard, and I find a loose kearney at the weatherhead. No problem so I unload the meter,pull it, tighten the connection...then I start noticeing, what to me is a suprise.
No main breaker at the pole, its been removed !!
Where the triplex lands on the house from the pole, it kearneys onto a #10 wire (among other unprotected connections) which was previously dead. This wire is unprotected and enters the house via going right into the mortar (limestone rock house) then goes across the length of the house via attic to the duo pack hvac unit with No protectection what so ever.
I reluctantely got the peoples "heat on", but called the landlord, and told her that she had a severe liability and it needed to be fixed asap....she said get-r-done
This make two of these type calls, Ive received this week...what keeps these people from being killed?
In this day and time, I wouldnt own one of those ratty ole rent house's for fear of being sued for may various reasons....couldnt sleep at night, knowing what I know.
So I got there, I asked what happend...the tennant said that they rented a dryer from a rent-to-own place, and the delivery guy had to put the cord on the dryer. Then he had to make an adjustment to the connection and it shocked him really bad, and he left. So I asked, "he did this while it was plugged in"? and they said yes....
So after checking checking around with my trusty wiggy, I find that there is no 240v in the house, only one leg or phase is hot, the other is very weak. So this leaves the hvac and the dryer unfunctional...
So this eventualy takes me out to the pole in the back yard, and I find a loose kearney at the weatherhead. No problem so I unload the meter,pull it, tighten the connection...then I start noticeing, what to me is a suprise.
No main breaker at the pole, its been removed !!
Where the triplex lands on the house from the pole, it kearneys onto a #10 wire (among other unprotected connections) which was previously dead. This wire is unprotected and enters the house via going right into the mortar (limestone rock house) then goes across the length of the house via attic to the duo pack hvac unit with No protectection what so ever.
I reluctantely got the peoples "heat on", but called the landlord, and told her that she had a severe liability and it needed to be fixed asap....she said get-r-done
This make two of these type calls, Ive received this week...what keeps these people from being killed?
In this day and time, I wouldnt own one of those ratty ole rent house's for fear of being sued for may various reasons....couldnt sleep at night, knowing what I know.