Appliance Disconnects in a commercial kitchen

Watt4

Member
I have a commercial kitchen with a large 3 phase 70 amp oven and 2- 3 phase 45 amp dishwashers and there is not one square foot of wall space to mount disconnect switches. Is it permissible to mount them in the accessible ceiling above the appliance if the switch is lockable?


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
A locking circuit breaker can serve as the disconnecting means if you comply with {see 422.31(B and (C))}
 