Having a bit of a discussion with a local inspector regarding GFCI protection for dishwashers in a new apartment complex. He says that we have to install a GFCI receptacle at the location of the dishwasher. I say that's a maintenance issue in the event the GFCI trips, requiring the removal of the dishwasher to re-set the GFCI and ask if we can put the dedicated circuit on a GFCI breaker. He claims, no. The code does not specify either, just that it shall be GFCI protected. I also suggested that we install a single receptacle for the dishwasher that is protected by a GFCI breaker. Any thoughts? Of course, all knowing that the authority having jurisdiction will typically dictate. Occasionally, if presented in the right way, inspectors can be convinced there are other ways to meet code and not be a maintenance issue.
 
Perhaps you could put a dead front GFCI receptacle in an accessible location, like on the wall just above the dishwasher.
 
A GFCI receptacle is not permitted behind a dishwasher because it must be readily accessible so the protection needs to be elsewhere in the circuit.
 
Thanks for the input. Using a dead front GFCI above the counter would be a great idea if we were still in the "rough-in "stages. Unfortunately, cabinets and tile have already been installed. Since these are small apartments, the panel is literally across the island of the kitchen. So, in most cases, within sight.
I also mentioned to him about being "readily accessible". We will go back to him to discuss further.

Thanks again, for your input!
 
Since you're going to need an arc fault breaker anyway, the incremental cost to have a dual function arc fault GFCI breaker is minimal. It may even be cheaper than a GFCI receptacle on an AFCI breaker.
 
I disagree with his assessment that it MUST be a GFCI receptacle and not a GFCI breaker. There is nothing to back up that position, unless it is some sort of local amendment to the NEC, and I can't for the life of me think of why that would have been done.
 
The inspector is clueless.
If you use a cord and plug method for the dishwasher the receptacle can not be behind the dishwasher. See 422.16 (B)(5). The GFCI can be a receptacle or a breaker. See 422.5(B).
 