Is a refrigerator and microwave considered a fastened in place appliance load that be applied to the 75% demand factor for four or more appliances?
220.52(A) exception says the refrigerator can be excluded from the SABC calc. If this is excluded can I included in the appliance load?
220.53 Appliance Load ? Dwelling Unit(s). It shall be
permissible to apply a demand factor of 75 percent to the
nameplate rating load of four or more appliances fastened
in place, other than electric ranges, clothes dryers, spaceheating
equipment, or air-conditioning equipment, that are
served by the same feeder or service in a one-family, twofamily,
or multifamily dwelling.
220.52(A) exception says the refrigerator can be excluded from the SABC calc. If this is excluded can I included in the appliance load?
You don't NEED to include it, it is already included in the SABC loads.
The exception to 220.52 says that if you provide the refrigerator with an individual branch circuit, you don't need to figure additional load for that circuit. (Are you trying to use it to get to 4 appliances so you can apply the demand?)