Appliance question

Status
Not open for further replies.

cppoly

Senior Member
Location
New York
If you have a motor operated or refrigeration appliance and the cut sheet does NOT indicate circuit breaker requirements, then what can be done in the following example:

Let's say you have a refrigerator that draws 1.2 amps:

1) Are you required to put this on a 15A breaker?
2) What rules to follow if connecting multiple units on the same circuit? Can I put three on? Five? What's the limit?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
If you have a motor operated or refrigeration appliance and the cut sheet does NOT indicate circuit breaker requirements, then what can be done in the following example:

Let's say you have a refrigerator that draws 1.2 amps:

1) Are you required to put this on a 15A breaker?
2) What rules to follow if connecting multiple units on the same circuit? Can I put three on? Five? What's the limit?
I don't see why it could not be on a 20 Amp circuit if that is what you are asking.
 

cppoly

Senior Member
Location
New York
Well for appliances that have motors or are refrigeration equipment, do you have to follow the OCPD rules in Articles 430 or 440 depending on what type of appliance it is? For instance, 1.2A x 225% = 2.7A = 15A max breaker?
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
You might want to read the 440.3(C) if you're talking about a household refrigerator.
 