Yes the OCPD can be either 15 or 20 amps with a single 20 amp receptacle. The receptacle is designed for both 15 and 20 amp plugs.Can an appliance with a NEMA 5-15 plug be plugged into a NEMA 5-20 simplex receptacle?
Breaker can be either 15A or 20A right?
I think the code requires the maximum OCPD be marked on the equipment nameplate.Thanks,
If a refrig appliance does not state the OCPD in the cut sheet, you have to calculate it? For instance if it says 5A current but does not say whether to use a 15A or 20A breaker, you can't exceed 15A OCPD if the calculation comes out to 11.5A right?
I don't think the code requires that for anything other than the equipment covered by Article 440. Per 440.3 plug in appliances that use hermetic refrigerant motor-compressors are covered by Article 422.I think the code requires the maximum OCPD be marked on the equipment nameplate.
I don't think that "Where appliance overcurrent protective devices that are separate from the appliance are required" applies to the branch circuit OCPD, but not sure.422.11 Overcurrent Protection.
(G) Motor-Operated Appliances. Motors of motor-operated
appliances shall be provided with overload protection in
accordance with Part III of Article 430. Hermetic refrigerant
motor-compressors in air-conditioning or refrigerating equipment
shall be provided with overload protection in accordance
with Part VI of Article 440. Where appliance overcurrent
protective devices that are separate from the appliance are
required, data for selection of these devices shall be marked on
the appliance. The minimum marking shall be that specified in
430.7 and 440.4.
I don't know if that sentence applies to refrigerators or not.