Problem:
I am allowed to use a 90°C conductor according to 110.14(C)(1)(b)(2)
I follow the 215.2(A)(1) to determine my conductor derate:
Taking the more conservative derate according to 215.2(A)(1) means my conductor ampacity derate needs to be 0.728. Now, because I am using 90°C conductor on a 75°C terminal the derates apply to the 90°C column in 310.15(B)(16). Finally, my interpretation of 110.14(C) says that this wire can only be used so long as the derated conductor ampacity results in a lower ampacity than the 75°C
From 110.14(C)
The temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor, or device. Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correct, or both.
From 110.14(C)(1)(b)(2)
Conductors with higher temperature ratings, provided the ampacity of such conductors does not exceed the 75°C ampacity of the conductor size used, or up to their ampacity if the equipment is listed and identified for use with such conductors.
Is this a correct understanding and application of conductor ampacity derates? In a situation where my combined ambient + CCC derate is lower than 0.8, then is it also correct to apply the continuous current derate to the 90°C wire and check that against the 75°C entry?
- I am trying to choose a 90°C conductor to land on my 75°C terminals.
- Equipment is 75°C rated.
- Equipment terminals are 75°C rated.
- Wire insulation is 90°C rated.
- Continuous load
- 40°C ambient temperature
- 4 current carrying conductors
I am allowed to use a 90°C conductor according to 110.14(C)(1)(b)(2)
I follow the 215.2(A)(1) to determine my conductor derate:
- 215.2(A)(1)(a): The load is continuous so I need at least a 0.8 derate (which is the inverse of 125%).
- 215.2(A)(1)(b):
- 40°C ambient temperature on 90°C conductor is 0.91 derate from Table 310.15(B)(2)(a).\
- 4 current-carrying conductors results in 0.8 derate from Table 310.15(B)(3)(a).
- Multiplying these together results in 0.728 derate.
Taking the more conservative derate according to 215.2(A)(1) means my conductor ampacity derate needs to be 0.728. Now, because I am using 90°C conductor on a 75°C terminal the derates apply to the 90°C column in 310.15(B)(16). Finally, my interpretation of 110.14(C) says that this wire can only be used so long as the derated conductor ampacity results in a lower ampacity than the 75°C
From 110.14(C)
The temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor, or device. Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correct, or both.
From 110.14(C)(1)(b)(2)
Conductors with higher temperature ratings, provided the ampacity of such conductors does not exceed the 75°C ampacity of the conductor size used, or up to their ampacity if the equipment is listed and identified for use with such conductors.
Is this a correct understanding and application of conductor ampacity derates? In a situation where my combined ambient + CCC derate is lower than 0.8, then is it also correct to apply the continuous current derate to the 90°C wire and check that against the 75°C entry?