Application of Tap Rule to DC Bus

Status
Not open for further replies.

LMAO

Senior Member
Location
Texas
I am thinking of tapping off a 820VDC bus. Do NEC tap rules apply to 820VDC? or is there a voltage limit (I can't find one)?

Also, when it says "taps not over 10 feet", is it talking about one way distance? or the total lenth of conductor?

Thanks
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I am thinking of tapping off a 820VDC bus. Do NEC tap rules apply to 820VDC? or is there a voltage limit (I can't find one)?
There are no voltage constraints I am aware of. I would point out that normal building wire is not rated for above 600 V.

Also, when it says "taps not over 10 feet", is it talking about one way distance? or the total lenth of conductor?
The definition of a tap includes the idea that it is a conductor so I would conclude it is the length of the conductor, not physical distance.
 