Inspector today told me I have to have the A.C. contractor for the new SFR I'm wiring install a breaker in the air handler unit because the a/h closet isn't big enough to comply with 110.26. He says I have to have 30 inches from side to side and 36 inches of depth in front of the disconnect (the working space requirements of 110.26). I've never run into this before in over 40 years in the trade.
I asked him about the disconnect for the 2nd a/h in the trusses over the garage and he said the same thing applied. With trusses centeed on 24 inches if the disconnect is mounted on the side of the truss its impossible to get 36 inches of clear depth. The next truss is only 22.5 inches away.
110.26 applies to equipment that might require working on it while energized. I don't know why anyone would have to work on a disconnect while it is energized.
I thought the disconnect was there to protect someone working on the air handler and wonder if it would even be required if the breaker feeding the a/h had lock off provisions installed on it.