Working on a project for a client of ours and came to a question regarding applying adjustment factor to cables.
The way the original switchboard was installed in the electric room allowed no room for expansion since it is installed tight up against a block wall. It is a 277/480V, 4000A switchboard and peak demand load history for the building shows they only use 1/3 of its capacity. They are out of breaker space in the switchboard and need room to add additional battery charger loads. We proposed to tap the bus of the existing gear cut a hole in the block wall and feed through to a new 4000A switchboard. We had the manufacturer look at it to verify a bus tap is possible and this was confirmed. I have attached an illustration and photo for reference.
Code reference implied below are from the 2008 NEC ? which is what Pennsylvania still uses.
The question is regarding the tap conductors. These will be installed free air inside the switchboard to through the wall, into the pull box for final connection to the new switchboard. Looking @ table 310.17 500?s are good for 620A (THHN,THWN) free air.
4000A /620A= 6.45 so a total of 7 sets.
However I am wondering if I will need to de-rate the cables per 310.15 (B) (2). If I must de-rate than it is a situation where the total number of cables is determined by the final de-rating factor.
Example ? (let?s assume Neutral is not a current carrying conductor, that?s another discussion entirely)
7 sets of 500?s = 21 current carrying conductors in all. So Table 310.15 (B)(2)(a) tells me adjustment factor of 45%
So using 90degree for de-rating of the 500?s (per 110.14 C)
700A x 45% = 315A
Therefore 4000A/315A = 12.6 Now I need 13 sets of paralleled 500?s??. but wait??..
13 sets = 39 current carrying conductors so now???
700A x 40% = 280A
Therefore 4000A/280A = 14.2. Now I need 15 sets of paralleled 500?s??..so now??..
15 sets = 45 current carrying conductors so now???
700A x 35% = 245A
Therefore 4000A/245A = 16.3. Now I need 17 sets of paralleled 500?s??..and I?ve finally reached rock bottom.
I cannot put the paralleled conductors in raceway within the gear so they will be installed for lengths longer than 24? without separation (exception #3) inside the gear. Am I over thinking this? Not the first time I?ve been ?accused? of doing that if I am .
The way the original switchboard was installed in the electric room allowed no room for expansion since it is installed tight up against a block wall. It is a 277/480V, 4000A switchboard and peak demand load history for the building shows they only use 1/3 of its capacity. They are out of breaker space in the switchboard and need room to add additional battery charger loads. We proposed to tap the bus of the existing gear cut a hole in the block wall and feed through to a new 4000A switchboard. We had the manufacturer look at it to verify a bus tap is possible and this was confirmed. I have attached an illustration and photo for reference.
Code reference implied below are from the 2008 NEC ? which is what Pennsylvania still uses.
The question is regarding the tap conductors. These will be installed free air inside the switchboard to through the wall, into the pull box for final connection to the new switchboard. Looking @ table 310.17 500?s are good for 620A (THHN,THWN) free air.
4000A /620A= 6.45 so a total of 7 sets.
However I am wondering if I will need to de-rate the cables per 310.15 (B) (2). If I must de-rate than it is a situation where the total number of cables is determined by the final de-rating factor.
Example ? (let?s assume Neutral is not a current carrying conductor, that?s another discussion entirely)
7 sets of 500?s = 21 current carrying conductors in all. So Table 310.15 (B)(2)(a) tells me adjustment factor of 45%
So using 90degree for de-rating of the 500?s (per 110.14 C)
700A x 45% = 315A
Therefore 4000A/315A = 12.6 Now I need 13 sets of paralleled 500?s??. but wait??..
13 sets = 39 current carrying conductors so now???
700A x 40% = 280A
Therefore 4000A/280A = 14.2. Now I need 15 sets of paralleled 500?s??..so now??..
15 sets = 45 current carrying conductors so now???
700A x 35% = 245A
Therefore 4000A/245A = 16.3. Now I need 17 sets of paralleled 500?s??..and I?ve finally reached rock bottom.
I cannot put the paralleled conductors in raceway within the gear so they will be installed for lengths longer than 24? without separation (exception #3) inside the gear. Am I over thinking this? Not the first time I?ve been ?accused? of doing that if I am .