Appropriate wire size for service

Status
Not open for further replies.

Mr. Serious

Senior Member
Location
Oklahoma, USA
Occupation
Electrical Contractor
I'm building a new 400-amp single-phase service for a property that has a 3000 square foot house, a pool and spa, a large shop building which will have several RV connections for occasional use, and a new 200 square foot building that will be a small business. I did a load calculation and came up with about 315 amps of load.

Originally I was planning to use a panel with a single 400-amp service disconnect breaker, but it turned out to be much cheaper to get a 400-amp main lug panel with room for six disconnects, following the six-disconnect rule that is allowed under code versions prior to 2020. Oklahoma is on the 2014 code revision.

I understand that when building a service with multiple disconnects, the main service wires need to be sized only to handle the anticipated load, not for the full 400 amps. However I had been planning to use 400-amp rated wire anyway. I was intending to use 2 parallel runs of 350kcmil Al in the same conduit, which should be big enough to carry 400 amps when de-rated for 4 current-carrying conductors in the conduit and for temperature.

But just yesterday, I was reading a post about services not really being rated for a continuous load. Main breakers are intended for a continuous load of up to 80% of their amp rating. Perhaps the bus bars of the panel itself are rated for a full continuous load of 400 amps. In the forum thread I was reading, someone said bus bars usually are rated for full continuous load. So, if the bus bars are rated for a continuous 400 amps and I install service wires also rated for a continuous load of 400 amps, would I really be building a 500-amp service?

As I said, the load calculation comes to about 315 amps, and load calculations done under the NEC rules are NOT a continuous load rating. They represent a minimum breaker size to be used for the service main breaker, so the load calculation number has already been increased to 125% of what it would be for a continuous load. So the homeowners could hypothetically add 85 amps of load and still be good with a hypothetical 400-amp breaker, if the service had one main disconnect breaker. The equivalent continuous load would be 320 amps. So, I'm thinking if I don't want to build this service too big, I ought to size my wire for 320 amps instead of 400. Or does it really need to be sized for 400, to allow for additional loads in the future?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You are not required to make it larger for future loads, that's a design issue. You can size the conductors for 315 amps and you're done. Your parallel 350's get you very near 450 amps so that should be plenty of room for expansion.
 

Mr. Serious

Senior Member
Location
Oklahoma, USA
Occupation
Electrical Contractor
I wanted to make it a little larger for future expansion because they talked about adding an electric car charger. So, maybe I'll stay with the 350 aluminum I had planned on.
 