Mike Meredith
Member
This has been touched on in earlier threads, but I didn't see a specific response. There is a practice currently in use of wiring duct dector shutdown contacts to a PLC or directly to a VFD circuit. Most OEM Cut Sheets for their duct detectors show the shutdown hardwired directly in the motor control start/stop circuit, and this seems to be the best practice.
However, I've found nothing in NFPA 90A or NFPA 72 that prevents landing the shutdown to a PLC, VFD, or other Automation Control. In my (poor) thoughts, if the device (PLC or VFD) is not listed for fire alarm service, then is it acceptable to interlock the Duct Detector to it?
Thanks...
However, I've found nothing in NFPA 90A or NFPA 72 that prevents landing the shutdown to a PLC, VFD, or other Automation Control. In my (poor) thoughts, if the device (PLC or VFD) is not listed for fire alarm service, then is it acceptable to interlock the Duct Detector to it?
Thanks...