Coastalguy1
- Virginia Beach, VA
(3) Height of Working Space. The work space shall be
clear and extend from the grade, floor, or platform to a height
of 2.0 m (61?2 ft) or the height of the equipment, whichever is
greater. Within the height requirements of this section, other
equipment that is associated with the electrical installation and
is located above or below the electrical equipment shall be
permitted to extend not more than 150 mm (6 in.) beyond the
front of the electrical equipment.
One solution might be to provide a (removable) work platform that covers the pipe, etc.It does not appear to me that the work space is clear as there is a pipe in the space.
That's what jumped out at me too, but the photo cuts it off just at the critical point. If that is over 6ft, then the rules allowing it are not being followed WRT support, starting with the fact that the first support must be within 12". And can you support it by clamping it to a gas pipe? I don't know, but I wouldn't even try that one.What is the length of the sealtite coming from the left bottom of disc. that runs along the gas line ?
Around here by the way, the AHJs would count BOTH pieces as cumulative in the 6ft rule, since they are the same circuit. I don't agree with their interpretation, but it's one of those things that's never been worth fighting over.
Re: the pipe in front of it, seems to me that I've seen this discussed in here before in the past, especially as it pertained to pump houses or swimming pool sheds.