Approved Wiring Methods for Shielded Signal Cable

Status
Not open for further replies.

gerbonic

Member
Location
Texas
Can someone direct me to the NEC article that covers signal cable like Belden 8760. I have seen different methods for installing signal cable around different installations and even seen it outside of a conduit in short runs. Is there anything that directs approved method for running this type of cable in power limited installation (4-20mA signal, etc)?

Thanks
 
Most likely its a Art 725 Class 2 circuit. If not its a Class 1 circuit which is wired using a chapter 3 method. The power supply determines the class.
725 can be a bit overwhelming, just take your time and go thru it.
 