Re: arc fault and plasma tv
If you still have access to the camp, I would remove both the hot and neutral from the breaker. Then using a continuity tester of some kind see if there is any continuity between either the hot or neutral to the ground buss. If there is then you will have to find out why.
There a few things that will cause an AFCI to trip when a load is applied:
1. A neutral to ground connection on the load side of the circuit.
2. The AFCI circuit is sharing the neutral with another circuit.
3. The AFCI's neutral has been inadvertently been connected with a neutral from another circuit.
4. A TVSS type device is being used on the AFCI circuit and the MOV's in it are at their end of life and are leaking to ground from neutral.
5. The TV's could have a neutral to ground leakage through the coax. Try un hooking the coax and see if they still trip.
Removing the code required AFCI's, could put you and your company at risk of a law suit if a fire broke out and the cause was a failure of having a AFCI in the circuit!!!
There could be a fire hazard if one or more of the above mention items are the reason the AFCI is tripping.
Trouble shoot it but never remove a device intended to protect life and property. Always find the cause even if it is the AFCI that causing the problem notify the manufacture and UL of the problem when the cause is found.
UL can be contacted by going to there web site at
www.ul.com. They have a page to submit problems.