Arc-fault breaker and gfic receptacles?

Status
Not open for further replies.

robert pitre

Member
Location
Houma,la
Some one please tell me this. I’m I understanding this right,that if there is a gfic receptacle being used for dish washer , Landry , kitchen receptacles on (gfic receptacles),dose this branch circuits still needs to be on the arc-fault/ gfic breaker? We are using Nec 2014 code book.
 
Just get arc/gfci combo breakers


Sent from my iPhone using Tapatalk
When you say AFCI/GFCI combo the meaning is clear, but the term combination or "combo" refers to combination parallel arc and series arc AFCI units.
The combination of AFCI and GFCI is properly referred to as "dual function".

Sent from my XT1585 using Tapatalk
 