No, because the switch (box) would not be considered an outlet. (depending on your code)Now if I run a 3 way back the house with a dead end 3 way switch in the house to control the outside lights at the garage do I need an arc fault breaker in the garage panel?
That's why I mentioned the code; we're still on '14 and only have to cover bedroom outlets.I disagree and would would say "yes" as you have a device (switch) in one of the dwelling unit rooms requiring AFCI.
The 2014 says "outlets or devices", a switch is a device.That's why I mentioned the code; we're still on '14 and only have to cover bedroom outlets.
Plus, whether switch boxes are considered to be outlets has been debated quite a bit here.
2014 code added kitchens and laundry to already included spaces of residential family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways or similar rooms.That's why I mentioned the code; we're still on '14 and only have to cover bedroom outlets.
Plus, whether switch boxes are considered to be outlets has been debated quite a bit here.
That is correct. Under the 2011 it wasn't required for a switch.Inspector I had when we first went to 2014 indicated the switch in a room area that would require and AFCI would require AFCI protection even if it only was controlling something outside of the required areas
Had GC get really bent over that, saying the light was outside and shouldn't need AFCI, inspector said "Nope, first terminations is inside required area."That is correct. Under the 2011 it wasn't required for a switch.
A switch is also an outlet.The 2014 says "outlets or devices", a switch is a device.
A switch is also an outlet.
I agree, especially as it pertains to something intended to mean receptacleThe reason they added the word device to the code on afci is because switches are not outlets, IMO
The term "outlet" is not intended to mean receptacle.I agree, especially as it pertains to something intended to mean receptacle
In 1965 my folks paid $20k for a 4-bdrm near Cal State Fullerton (LA suburb) w/ detached garage, which sold "As Is" to a house flipper for $650k in 2018.I have a detached garage with feeder from the house to the garage, Now if I run a 3 way back the house with a dead end 3 way switch in the house to control the outside lights at the garage do I need an arc fault breaker in the garage panel?
I think I didn't say it right earlier because my two posts look conflicted.The term "outlet" is not intended to mean receptacle.
While a receptacle is a special type of outlet, the connection between the branch circuit wiring and the utilization equipment is an outlet. All equipment is connected to an outlet.
I thought the same thing.A wireless 3-way switch avoids new work NEC 210.12 at house, when paired with similar 3-way switch at detached garage (AFCI exempt)
A switch is not an outlet and that is why the term "device" was added to the AFCI rule a couple of cycles ago.I think I didn't say it right earlier because my two posts look conflicted.
I agree that an outlet is any receptacle, switch, light, smoke detector, or any other equipment. I don't believe junction boxes are outlets.
...
It seems you're wavering back and forth between what constitutes an outlet in a general sense versus an outlet as it pertains to an afci circuit.A switch is not an outlet and that is why the term "device" was added to the AFCI rule a couple of cycles ago.
It seems you're wavering back and forth between what constitutes an outlet in a general sense versus an outlet as it pertains to an afci circuit.
We're talking past each other I think