I have ane arc fault SQ D HOM 20A that trips when it is energized. There are a couple of illuminated toggle dimmer switches on that circuit , but otherwise there is no load plugged in. This is an older installation and i tried to retrofit and arc fault into the system. Has anyone had problems with this type of dimmer and an arc fault. What else could it be.
OK. By your description, I understand you to say, you have an existing branch circuit (BC). I assume that you didn't install that BC originally, and that part, if not all, of it is covered by wall surface, so you can't examine it.
Sounds like you've mapped the circuit and know every box that is on it.
- Remove the load wires from the breaker (leave the line neutral connected) and turn it back on. Tripping indicates bad breaker.
- Look for continuity between the BC neutral and the equipment ground. If it is there, it needs to be removed.
- If the BC neutral is cross connected to another circuit's neutral, say in a multi switch box, or if the original BC was a multiwire, that will trip the AFCI.
There's more, but first, is any of this ringing a bell?