FWD

Member
For a service upgrade on an existing building with two meters one for a sub panel serving the residence one for a sub panel serving the commercial portion . As this is a mixed use commercial with residential dwelling in one building will arc fault breakers required in the commercial panel ?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Barring local ordinances, if you don't alter or extend branch circuits AFCI does not need to be addressed in either. see 210/12(D) for exceptions.
 

JohnE

Senior Member
Location
Milford, MA
Upgrading the service doesn't trigger anything to mandate installation of arc-fault breakers, unless it is a local requirement, in the residential or commercial space.
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
And, to augment Augie's observation and NEC citation, which was from the 2017 NEC, and I note that your profile has you under the 2014. The exception Augie is referring you to changed number location between the 2014 and 2017. In the 2014 NEC read 210.12(B) Exception.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
And, to augment Augie's observation and NEC citation, which was from the 2017 NEC, and I note that your profile has you under the 2014. The exception Augie is referring you to changed number location between the 2014 and 2017. In the 2014 NEC read 210.12(B) Exception.

You shouldn't "augment Augie" he's old!:)
 