ARC Fault breakers when doing a panel update

Status
Not open for further replies.

ericmccurley

Member
Location
Arkansas
Occupation
Electrician
So article 210.8 (A) reads all 125 V, single phase 15 and 20 amp receptacles installed in the location specified in 210.8 a one through 10 shall have ground fault circuit interrupter protection for personal. However, when doing a service upgrade/panel upgrade no local inspector has stated that I need to install arc breakers. I'm assuming that it has to do with my local codes? Also, and I'm more interested in this question. If I install arc fault breakers when I do a panel upgrade or service upgrade at a house that has been wired back in the 40s 50s or 60s with all the neutrals shared in the electrical system. Would I have problems down the road with the customer, calling me back for arc fault, breakers continually tripping from shared neutrals? My experience tells me yes, and I don't want to take the risk and find out. But I guess I don't understand electrical theory well enough to figure this out and I have zero experience because I have never been required to do this.
 
210.12(D) fairly well covers the 1st part of your question.
Yes, shared neutrals would create a problem if you installed AFCI breakers.
 
So article 210.8 (A) reads all 125 V, single phase 15 and 20 amp receptacles installed in the location specified in 210.8 a one through 10 shall have ground fault circuit interrupter protection for personal. However, when doing a service upgrade/panel upgrade no local inspector has stated that I need to install arc breakers. I'm assuming that it has to do with my local codes? Also, and I'm more interested in this question. If I install arc fault breakers when I do a panel upgrade or service upgrade at a house that has been wired back in the 40s 50s or 60s with all the neutrals shared in the electrical system. Would I have problems down the road with the customer, calling me back for arc fault, breakers continually tripping from shared neutrals? My experience tells me yes, and I don't want to take the risk and find out. But I guess I don't understand electrical theory well enough to figure this out and I have zero experience because I have never been required to do this.

I like your logo ! I would put a disclaimer on my invoices "Not Responsible For GFCI/AFCI Installed after 60 Days".
 
So article 210.8 (A) reads all 125 V, single phase 15 and 20 amp receptacles installed in the location specified in 210.8 a one through 10 shall have ground fault circuit interrupter protection for personal. However, when doing a service upgrade/panel upgrade no local inspector has stated that I need to install arc breakers. I'm assuming that it has to do with my local codes? Also, and I'm more interested in this question. If I install arc fault breakers when I do a panel upgrade or service upgrade at a house that has been wired back in the 40s 50s or 60s with all the neutrals shared in the electrical system. Would I have problems down the road with the customer, calling me back for arc fault, breakers continually tripping from shared neutrals? My experience tells me yes, and I don't want to take the risk and find out. But I guess I don't understand electrical theory well enough to figure this out and I have zero experience because I have never been required to do this.
please disregard this post as my reference to 210.8 is clearly wrong. Article 210.12 is what I am referring too.
 
The NEC doesn't require AFCI's on a panel upgrade as long as the existing circuits aren't extended more than 6'. I just changed out a panel with no new AFCI's.
 