While calculating the arc fault on the secondary of a 150 kva transformer, I'm challenged with calculating the time duration until the fault will clear.
Scenario: Utility supplies 21,000 AIC , 208, 3 ? to the customers 400 amp fused disconnect. The time current curve for these fuses will clear at .01 seconds at 11,000 amps. Ten feet of Conduit to a 150 kva transformer.
208 Y to a 240 ▲ Z=4.8% The Secondary of the transformer is in conduit for about ten feet to a breaker.
Question: How to determine the clearing time of the upstream fuses (400 amp @ the main Disconnect) when a fault occurs on the secondary of the transformer, before the down stream breaker comes into play? Note: the calculated available fault current on the secondary of the transformer is about 8,600 or so. Will this available fault current produce enough current on the primary to open the main fuses in a timely matter?
Thanks
Scenario: Utility supplies 21,000 AIC , 208, 3 ? to the customers 400 amp fused disconnect. The time current curve for these fuses will clear at .01 seconds at 11,000 amps. Ten feet of Conduit to a 150 kva transformer.
208 Y to a 240 ▲ Z=4.8% The Secondary of the transformer is in conduit for about ten feet to a breaker.
Question: How to determine the clearing time of the upstream fuses (400 amp @ the main Disconnect) when a fault occurs on the secondary of the transformer, before the down stream breaker comes into play? Note: the calculated available fault current on the secondary of the transformer is about 8,600 or so. Will this available fault current produce enough current on the primary to open the main fuses in a timely matter?
Thanks