Sparky2791
Senior Member
- Location
- Northeast, PA
- Occupation
- Electrical Design
Hello!
I have a reno project of a building that was constructed in the 1990’s. We had an arc flash hazard analysis study performed on the entire electrical system (new and existing) which has resulted in 3 existing panelboards failing.
These are in a section of the building not being renovated. The arc fault current at the panel is shown to be higher than the panelboards rating which is of course based on the AIC of the circuit breakers installed.
From a safety standpoint I know the proper thing to do is to correct this. We have requested a change order from the contractor to add fused switches ahead of each of the panels to reduce the AIC @ the panelboard.
Does the NEC address this in anyway? 110.16 is not specific to that. I suppose it falls under maintenance while the NEC is regarding new installation.
This is for a 100A,200A & 400A branch circuit panelboard.
Thanks for your comments
I have a reno project of a building that was constructed in the 1990’s. We had an arc flash hazard analysis study performed on the entire electrical system (new and existing) which has resulted in 3 existing panelboards failing.
These are in a section of the building not being renovated. The arc fault current at the panel is shown to be higher than the panelboards rating which is of course based on the AIC of the circuit breakers installed.
From a safety standpoint I know the proper thing to do is to correct this. We have requested a change order from the contractor to add fused switches ahead of each of the panels to reduce the AIC @ the panelboard.
Does the NEC address this in anyway? 110.16 is not specific to that. I suppose it falls under maintenance while the NEC is regarding new installation.
This is for a 100A,200A & 400A branch circuit panelboard.
Thanks for your comments