From the website:
*Delete Subsection (B) ?Dwelling Units? of Section 210.12 ?Arc-Fault Circuit-Interrupter Protection? and substitute the following:
210.12 Arc-Fault Circuit-Interrupter Protection.
(B) Dwelling Unit Bedrooms. All 120-volt, single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit bedrooms shall be protected by a listed arc-fault circuit interrupter to provide protection of the branch circuit.
FPN: For information on types of arc-fault circuit interrupters, see UL 1699-1999, Standard for Arc-Fault Circuit Interrupters.
Exception: The location of the arc-fault circuit interrupter shall be permitted to be at other than the origination of the branch circuit in compliance with (a) and (b):
(a)
The arc-fault circuit interrupter installed within 1.8m (6 ft) of the branch circuit overcurrent device as measured along the branch circuit conductors.
(b)
The circuit conductors between the branch circuit overcurrent device and the arc-fault circuit interrupter shall be installed in a neutral raceway or a cable with a metallic sheath.
(Effective January 1, 2009; AMENDMENT EXPIRES JANUARY 1, 2010)
End of Amendments.
GA Electrical Code (National Electrical Code) Amendments 2009 3