Arc fault in main panel tripping due to grounds and neutrals bonded

Status
Not open for further replies.

redeemed1

Member
Location
austin,tx.
Could the arc fault breaker be tripping due to the neutrals being bonded in a main panel? The breaker is a GE pigtail stab in type


Sent from my iPhone using Tapatalk
 
Could the arc fault breaker be tripping due to the neutrals being bonded in a main panel? The breaker is a GE pigtail stab in type


Sent from my iPhone using Tapatalk
No. the load side of breaker neutral needs to fault to ground for "ground fault" trip feature to be the reason for the trip. The panel neutral bus even though it is bonded at a service panel is on the supply side of the AFCI device.
 
No. the load side of breaker neutral needs to fault to ground for "ground fault" trip feature to be the reason for the trip. The panel neutral bus even though it is bonded at a service panel is on the supply side of the AFCI device.

Thank you


Sent from my iPhone using Tapatalk
 