Arc-Fault in upgrade panel

Status
Not open for further replies.

steelbuster

Member
Location
mn
I am doing a service panel upgrade only (100Amp to 200Amp)in an older dwelling with very few equipment grounds. Will Arc-Fault breakers be required for the bedrooms due to the panel change?
 

bphgravity

Senior Member
Location
Florida
Re: Arc-Fault in upgrade panel

I would strongly recommend it. The closer you bring existing installations to current code the more limited your liability becomes. My jurisdiction has made the dscision to require this and we look for compliance on inspection. Some have complained that the afci's are not compatible in all cases with the existing wiring and circuit design, however our building director feels the afci protection is more important than the contractors conveniency or ease of work.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Re: Arc-Fault in upgrade panel

In my jurisdciction, recommended, not required--unless you install a new circuit.
 

steelbuster

Member
Location
mn
Re: Arc-Fault in upgrade panel

OK,thanks. GE's instructions for instalation of their AFI's, says to use "only 2 conductor with ground cable such as NM-B". If that is the manufacturers requirement will it be out of compliance when used with old NM cable without a ground?
 