Can two single pole AFCIs be used on a 14/3 circuit, 2 - 15 amp circuits sharing the same neutral. Or does a 2 pole AFCI have to be used?
Maybe I'm weird, but that reads as kind of an insult, to me.Originally posted by kalanjeya:
walton , u have to study more about working priciples of protection devices.
Jeyakumar
AFCIs have built-in GFCI circuity, the tying of neutrals together will cause a trip.Originally posted by walton:
Looking at the one line of a Cutler-Hammer AFCI, I don't see why you could not use two singles with the neutral spliced to both AFCIs. The answer must be in the Logic Trip.
Are you refering to the 14-2-2 NM cable? You are correct in that you would have to apply an ampacity adjustment, but you also have to if you had the same amount of conductors in a raceway. At any rate, (4) 14 gauge current carrying conductors is a moot point, as the adjusted ampacity is 20 amperes (25 times 80%). When you consider the rules of 240.4(D) and 334.80, it is a wash.Originally posted by DaveTap:
Oh great!! Now we get to de-rate Romex and UF... I'll stick to conduit.
Are you using this wire? I remember when it came out a few years ago but I have not seen much of it since then.Originally posted by wyatt:
you can use 14/4 new wire thats out.