Is arc fault protection now required for lighting in residential?
Jeff
Jeff
Arc fault protection is required for all branch circuits supplying "Outlets" in the areas specified in 210.12. The definition of "Outlet" from Article 100 of the NEC includes lighting outlets. This is not a new change in the NEC as the requirements in the 2002 NEC included the term "Outlet".
Chris
What he was trying to say is that AFCI protection was required for all "outlets" in the rooms mentioned in 210.12. But in 2002 the only "rooms" mentioned in 210.12 was bedrooms.I don't have the 2002 but wasn't that just for bedrooms at that time.