I need to add a receptacle in a basement near a wet bar. The walls and ceiling are finished drywall so I cannot get a new circuit to this area without cutting drywall or running surface mount. I am able to fish a wire from an existing receptacle located above the counter on the bar. This is on a 3-wire circuit with a shared neutral to a dishwasher under the bar.
My inspector is requiring any new wiring in this area have arc fault protection. My supply house told me Square D does not yet make a QO (not Homeline) series 2-pole 20 amp arc fault breaker.
I don?t think a single pole arc fault breaker will work properly on one circuit of this 3-wire circuit with a shared neutral.
The inspector told me he would allow me to convert the 3-wire circuit to a 2-wire and put the dishwasher and receptacles on the same circuit. There will only be a couple convenience outlets on the same circuit with the dishwasher. Then I could use a single pole arc fault breaker.
Should I expect any problems with a dishwasher on an arc fault breaker? Any other ideas?
Thanks.
My inspector is requiring any new wiring in this area have arc fault protection. My supply house told me Square D does not yet make a QO (not Homeline) series 2-pole 20 amp arc fault breaker.
I don?t think a single pole arc fault breaker will work properly on one circuit of this 3-wire circuit with a shared neutral.
The inspector told me he would allow me to convert the 3-wire circuit to a 2-wire and put the dishwasher and receptacles on the same circuit. There will only be a couple convenience outlets on the same circuit with the dishwasher. Then I could use a single pole arc fault breaker.
Should I expect any problems with a dishwasher on an arc fault breaker? Any other ideas?
Thanks.