Does the lighting circuit in a bathroom need to be arc fault protected, and I am installing a vent fan inside a shower enclosure. I’m assuming it needs to be GFI protected?
They finally weaseled AFCI into bathrooms? Which code cycle (s)?The AFCI will depend on the code edition you are on.
Where does it say that?2020 NEC may require GFCI protection if outlet is within 6 feet of water?
2023 clarifies the bath fan receptacle, within the unit, does not require GFCI protection unless required by the manufacturer. IE, usually only if over a tub or shower.2020 NEC may require GFCI protection if outlet is within 6 feet of water?
2023 clarifies the bath fan receptacle, within the unit, does not require GFCI protection unless required by the manufacturer. IE, usually only if over a tub or shower.
Every three years.There is already a new NEC Code book? I have 2020